[mythtvnz] RG6 cable and mains power cable fed through same junction box - interference likely?

yuri mythtvnz@lists.linuxnut.co.nz
Sat, 19 May 2007 10:42:55 +1200


On 18/05/07, Noel & Di wrote:
> It's important to maintain segregation of services - ie an insulated
> insert in the double flush box to keep the coax and TPS apart -
> otherwise all conductors & cables must be insulated for 230V to comply
> with the regs.  The old 70's style point with integral ribbon socket is
> contrary to the current regs because it provides inadequate segregation
> of LV (230V) and ELV wiring systems.  Normally a minimum separation of
> 100mm between power & data/Av with avoidance of parallel cable runs is
> recommended to minimize EMI.
> Noel

What Noel said!
The wiring rules (AS/NZS 3000:2000) don't allow these fittings in the
same flush box unless the RG6 is insulated for 230V.

The interference would be minimal. The shock hazard would be small but
not small enough to satisfy electrical regulations.

Bottom line - you just can't legally do it, even if it wouldn't really
be a problem.

Yuri