[chbot] Scrounging for big switch mode PSUs
Mark Atherton
markaren1 at xtra.co.nz
Thu Mar 7 23:44:09 GMT 2019
As long as the outputs of the units are floating, then 3 x 48V in series
sounds easiest.
Strongly recommend that you do a 'megger' type test on each unit first
though: With the units unpowered, connect together plus and minus
outputs, then do 500V insulation test between joined outputs and chassis.
-Mark
On 8/03/2019 12:12 PM, Robin Gilks wrote:
> Hi All
>> As part of my domestic grid tied battery system I need an isolated DC
>> power
>> supply capable of producing 2.5kW at between 120V & 300V The voltage does
>> not need to be adjustable.
>>
>> My plan is to purchase 3 x 1000W 48V caged units and series them to yield
>> 3kW @ 144V however I thought I'd see what folks have gathering dust before
>> I place the order. There a many configurations that would do the trick 2
>> or
>> 3 x 76V or 96V or even a stack of meaty 24V units.
>>
>> If you have a suitable combination you would like to dump, sell or swap
>> for
>> beer please let me know.
>>
>> Peter